The following tables list and describe the parameters specific to the UIS command component types for this remote device:
For more general information about UIS command component parameters, see UIS Command Components. The DG_F_DEV (Get data group from device) and DG_T_DEV (Send data group to device) command component types are configured in the template file. The other command component types are considered ‘special’ and are defined in the EIE editor code. See Special UIS Command Component Types for more information.
|
Update CygNet Point updates the record for a CygNet point. CYUPDTPT has the following command parameters:
|
|
Wait for CygNet Point signals the UIS to wait to perform a command until the value of the specified CygNet point changes to a specified value. CYWAITPT must be the first command component added to a UIS command. You cannot add other instances of CYWAITPT to a UIS command. CYWAITPT has the following command parameters:
|
Get data group from device retrieves a data group from a field device. The Parent XML Element is uccRecvParms. The following parameters are available for each specified data group type.
| Data Group Type | Parameter | Required | Description |
|---|---|---|---|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. Default = 0 for all. |
|
|
ForceCfg |
No |
Force reconfiguration Value options are Boolean. Default = false. |
|
|
Ack |
No |
Acknowledge/Clear Events, when specified, acknowledges and clears device events. Value options are Boolean. |
|
|
Ack |
No |
Acknowledge/Clear Events, when specified, acknowledges and clears FMS alarm events. Value options are Boolean. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
Ack |
No |
Acknowledge/Clear Events, when specified, acknowledges and clears FMS events. Value options are Boolean. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest
|
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
Cnt |
No |
Max Records to Read specifies the maximum possible number of records to read in a single transaction. The highest value possible for Max Records to Read is 960 or the size of the field device buffer if it is less than 960. Subsequent transactions might be required to retrieve all required data. If not specified, all remaining records will be read. Value options are integers. |
|
|
EDate |
No |
End Date defines the ending date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
No |
Start Date defines the starting date and time for a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: If you specify GetLatest="true", a start date or end date is not required. If GetLatest="false", a start date is required. |
|
|
Seq |
No |
Starting Sequence Number defines the first sequence number in the requested range. Value options are integers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single Coil data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single Coil - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 2-Byte Reg data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 4-Byte Reg data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 2-Byte Reg - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 4-Byte Reg - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
Send data group to device sends a data group to a field device. The parent XML Element is uccSendParms. The following parameters are available for each specified data group type.
| Data Group Type | Parameter | Required | Description |
|---|---|---|---|
|
DriftSpec |
No |
Delta Seconds Allowed |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single Coil data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single Coil" (SnglCoil) data group. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single Coil - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single Coil - Realflo Addr" (SnglCoilRF) data group. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 2-Byte Reg data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single 2-Byte Reg" (SnglReg2) data group. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 4-Byte Reg data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single 4-Byte Reg " (SnglReg4) data group. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 2-Byte Reg - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single 2-Byte Reg - Realflo Addr" (SnglReg2RF) data group. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down list in the Single 4-Byte Reg - Realflo Addr data group dialog box. |
|
|
Desc |
No |
Description Value options are strings. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
RegNum |
Yes |
Register Number specifies the register number used to retrieve data from a single element. Value options are valid register numbers. |
|
|
Value |
Yes |
Value defines a value to be sent to a "Single 4-Byte Reg - Realflo Addr" (SnglReg4RF) data group. |